一个400平方的ktv,走道22米,需要设置强排烟吗?

一个400平方的ktv,走道22米,需要设置强排烟吗?

消防小饶 | 2023-12-30 21:44
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

同同不同 2023-12-31 09:06 00 [回复]举报

应设置排烟设施,若自然排烟满足要求也可设置自然排烟

消防网友16289 2023-12-31 13:00 00 [回复]举报

走道22m,可不设计排烟设施。但kTV房间由于考虑隔音效果,一般都是无窗房间,若一个房间大于50㎡应设排烟或无窗房间总建筑面积大于200㎡就需要设计排烟。这种情况小于50㎡的房间你可考虑在房间设计排烟口还是通过过道设计机械排烟解决!

后福快来 2023-12-31 18:37 00 [回复]举报

走道大于20米应设置排烟系统,排烟可以利用自然排烟窗,不具备自然排烟条件应设置机械排烟,同时如果KTV在4层排烟要求是全都要有

龙虾   回复: 后福快来2023-12-31 20:27

你要看在哪 4楼有的地方不让开ktv

0    0 [回复]举报

赵晓亮 2024-01-01 16:04 00 [回复]举报

你好,强排烟指的是机械排烟吗?

请参考,建筑防烟排烟系统技术标准 GB51251-2017

4.1.1 建筑排烟系统的设计应根据建筑的使用性质、平面布局等因素,优先采用自然排烟系统。

4.6.3 除中庭外下列场所一个防烟分区的排烟量计算应符合下列规定:     1 建筑空间净高小于或等于6m的场所,其排烟量应按不小于60m³/(h·㎡)计算,且取值不小于15000m³ /h,或设置有效面积不小于该房间建筑面积2%的自然排烟窗(口)。


建筑防火通用规范 GB55037-2022

8.2.2 除不适合设置排烟设施的场所、火灾发展缓慢的场所可不设置排烟设施外,工业与民用建筑的下列场所或部位应采取排烟等烟气控制措施:6 设置在地下或半地下、地上第四层及以上楼层的歌舞娱乐放映游艺场所,设置在其他楼层且房间总建筑面积大于100㎡的歌舞娱乐放映游艺场所;10 民用建筑内长度大于20m的疏散走道。

潘天坤 2024-06-17 20:16 00 [回复]举报

民用建筑内长度大于20米的疏散走道需要设置排烟设施

KTV设置在几层?这栋建筑一共多少层,建筑高度是多少?

场所内排烟设施的设置需要综合考虑,房间是否需要排烟,房间及走道现有排烟设施是否符合要求,是否存在大于50平方米的无可开启外窗的房间