消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防泵房上面有卫生间可以吗

消防泵房上面有卫生间,这个设置合理吗?

逗你玩儿 | 2023-07-04 17:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

安洪全 2023-07-04 17:31 00 [回复]举报

合不合理的不清楚,至少满足规范的平面布置要求。

规范只对消防泵房的布置楼层、防火分隔、疏散、装修材料等做了要求。

如果膈应的话,做好防水,下水管路布置的时候远离水泵及控制柜。

逗你玩儿   回复: 安洪全2023-07-05 09:39

多谢

0    0 [回复]举报

南明离火 2023-07-04 17:32 00 [回复]举报

没啥毛病吧 规范没说不允许啊

逗你玩儿   回复: 南明离火2023-07-05 09:39

就感觉怪怪的

0    0 [回复]举报

同同不同 2023-07-04 17:47 00 [回复]举报

上下水走泵房么?虽印象里没有明确规定不行,但考虑上下水走泵房会增加隐患,不建议这么设置,若卫生间上下水不走泵房,且卫生间地面防水满足要求,应该没问题

逗你玩儿   回复: 同同不同2023-07-05 09:38

多谢

0    0 [回复]举报

风无心 2023-07-04 20:23 00 [回复]举报

从规范的角度讲,消防水池不算有严格卫生要求的房间,但是泵房里面也有控制柜,万一漏水在控制柜里面,影响消防系统也不行,我也不建议这么做,实在没有办法的话,应该采取同层排水方式,并加强卫生间防水做法。

逗你玩儿   回复: 风无心2023-07-05 09:38

多谢

0    0 [回复]举报

关闭

关闭

手机APP下载