消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

【常见问题】室外消火栓动压不足,倒流防止器前未增设室外消火栓

发布于:2024-11-10 16:53

【问题描述】室外消火栓动压不足;倒流防止器前未增设室外消火栓。

 

《消防设施通用规范》GB55036-2022

3.0.3 设置市政消火栓的市政给水管网,平时运行工作压力应大于或等于0.14MPa,应保证市政消火栓用于消防救援时的出水流量大于或等于15L/s,供水压力(从地面算起)大于或等于0.10MPa。

 

3.0.4-2 当室外消火栓系统的室外消防给水引入管设置倒流防止器时,应在该倒流防止器前增设1个室外消火栓;

 

 

 

 

 

来源:青岛市建设工程消防验收给排水专业常见问题(2024版)


请写下您的评论评论
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


评论 | 0
推荐问答

关闭

关闭

手机APP下载