消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

防烟分区的风管耐火等级

防火分区和防烟分区的排烟风管耐火等级是否一样?防烟分区的镀锌板风管是否要防火包裹

徐哥 | 2024-09-08 15:15
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消防网友68723 2024-09-09 11:02 00 [回复]举报

一样的

磊中 2024-09-09 11:15 10 [回复]举报

你说的是排烟管道和送风管道吧?

都一样的防排烟管道都一样的

规范说的是吊顶内的排烟管道应采用不然材料

隔热,并应与可燃物保持不小于150mm的距离

无糖可乐 2024-09-09 14:06 00 [回复]举报

排烟风管要求耐火极限,并非耐火等级。对于消防排烟系统的排烟风管的耐火极限应符合GB51251-2017第4.4.8条规定。镀锌钢板风管无法满足要求,需要采取防火包裹措施。

潘天坤 2024-09-10 08:10 00 [回复]举报

水平设置的排烟管道,当设置在非走道的吊顶内,其耐火极限不应低于.5小时;

水平设置的排烟管道,当设置在走道的吊顶内,其耐火极限不应低于1小时;

水平设置的排烟管道,当设置在非吊顶内,其耐火极限不应低于1小时;

水平设置的排烟管道,当设置在汽车库,其耐火极限不应低于0.50小时;

上述为烟规GB51251的要求,在不穿越防火分区、防火隔墙的情况下还应满足相关耐火极限要求,当穿越防火分区或者防火隔墙应按照规范要求相应提高耐火极限要求

关闭

关闭

手机APP下载