汽车库有防烟分区长边小于70m的规定么?

看到一份图纸,上面说防烟分区长边小于70m是合格的,哪个规范有这个规定么?

花生12138 | 2024-07-10 14:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

潘天坤 2024-07-11 14:33 10 [回复]举报

从烟规GB51251及汽车库规范GB50067来说,均未提到汽车库防烟分区的长边最大允许长度要求,如果没有地区技术文件规定,个人觉得可能没办法强制要求该如何执行

个人认为可以参照烟规GB51251要求,并进行放宽,例如是否考虑将汽车库防烟分区的长边最大允许长度要求参照烟规GB51251放宽到60米或者75米,建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准

上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

汽车库、修车库、停车场设计防火规范 GB50067-2014内仅提到“防烟分区的建筑面积不宜大于2000㎡”,并未提及汽车库防烟分区的长边最大允许长度要求,

建筑防烟排烟系统技术标准 GB51251-2017仅提到:汽车库防烟分区的划分及其排烟量应符合现行国家规范《汽车库、修车库、停车场设计防火规范》GB 50067的相关规定,并未提及汽车库防烟分区的长边最大允许长度要求

GANSTER 2024-07-26 08:49 00 [回复]举报

汽车库排风兼排烟风管及排风口沿车库防烟分区尽量做到均匀布置的前提下(个人控制在风口离防烟分区尽端不超过15米),从排烟角度考虑防烟分区长度可以不限,因为不存在烟气长距离射流卷吸冷空气下沉的可能。但另一个角度看,防烟分区太长会导致管线过长,从而使得风机压头增大理论上不利于节能运行,之所以称理论上是因为车库排风机平时大多数情况下一年估计也用不了一次。