消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

敞开式外廊能否装可开启外窗?

护幼保健中心的敞开式外廊能不能装可开启外窗?

凤鸣九天 | 2024-06-01 12:27
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 9

我头发贼黑 2024-06-01 17:51 00 [回复]举报

那就不叫敞开了

懒得说 2024-06-02 07:58 00 [回复]举报

敞开式外廊安装窗户?是不是描述有问题

黄-江西省景德镇市 2024-06-02 11:48 00 [回复]举报

问题描述确实欠佳。敞开式外廊如果沿着外侧做窗户,那么就形成内走廊了,就不叫外廊了,开窗做自然排烟是必须的,而且还要根据建筑高度、层数等等考虑设置封闭楼梯间和及其他设施。

凤鸣九天   回复: 黄-江西省景德镇市2024-06-02 23:34

有窗户的外走廊能否当成敞开式外廊?总开口面积有百分之五十这么大

0    0 [回复]举报

黄-江西省景德镇市   回复: 凤鸣九天2024-06-04 12:55

建议类似问题附现场图片或图纸+标注,否则无法明白现场到底是啥情况。

另,敞开式外廊是不计入建筑面积的,也就是说敞开式外廊属于室外,做了一部分窗户就可以认为是室内部分,要考虑窗会起到挡烟作用,烟气不会直接排向室外而影响疏散,还会沿原敞开式楼梯间蔓延至上层空间,即使有50%的敞开面积,这个也只能当成是自然通风口(窗)来定义,但会影响整个层面的防火分隔。消防各个专业之间是存在链条效应的,一个专业改了就可能导致全局的修改。

0    0 [回复]举报

潘天坤 2024-06-03 08:53 00 [回复]举报

如果是敞开式外廊,并且开口在走道净高的二分之一以上,同时开口满足规范要求,理论上不需要再设置自然排烟窗了呀。

新雪无痕 2024-06-03 09:26 00 [回复]举报

装上窗户封闭起来就不是敞开式外廊了

phone0224 2024-06-03 09:45 00 [回复]举报

性质完全变了

小北1982 2025-07-05 08:34 00 [回复]举报

人家楼主想问的应该是敞开连廊一侧设开启外窗,是否违背防火规范关于2m防火保护距离的问题!

关闭

关闭

手机APP下载