想让大家看看或者说批改下。一个茶业店我把它定性为中危1级场所,建筑面积为518㎡。我计算得计算单元内最小需配灭火级别为4A,设置点为2个,设置点内最小需配灭火级别为2A,每个设置点灭火器数量为2具。请问下大家是否正确呢?

平心 | 2023-11-18 20:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

安洪全 2023-11-20 09:32 20 [回复]举报

中危险1级是自喷中的概念,四类八级。

灭火器是高、中、低三档。

只知道面积的话,计算点位,略微有点不严谨,点位不仅对保护面积有要求,对间距也有要求,如果户型奇葩,间距超保护要求的话,可能覆盖不住。

平心   回复: 安洪全2023-11-22 20:01

谢谢

0    0 [回复]举报

阳明心 2023-11-20 11:27 10 [回复]举报

表6.2.1 A类火灾场所灭火器的最低配置基准
A类火灾场所灭火器的最低配置基准

计算单元最小需配置8A, 设置点2个时,设置点最小需配灭火级别4A, 每个设置点灭火器2具。

平心   回复: 阳明心2023-11-22 20:01

谢谢

0    0 [回复]举报