自喷系统控制方式

自动喷淋系统需要同时设置几种不同的方式连锁启泵吗?

patrick | 2023-09-06 12:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-09-06 14:10 10 [回复]举报

不需要同时设置多种,选择其中一种即可。

张治福 2023-09-06 15:05 10 [回复]举报

条文解释里有说明:

这三条是根据目前国内外自动喷水灭火系统消防水泵启泵方式的应用现状,分别规定了不同类型自动喷水灭火系统消防水泵的启动方式,并与国家标准《消防给水及消火栓系统技术规范》GB 50974 协调一致。需要说明的是,规定不同的启泵方式,并不是要求系统均应设置这几种启泵方式,而是指任意一种方式均应能直接启动消防水泵。