汽车库入口在火灾状态下能否作为汽车疏散出口?

地下一层Ⅱ类汽车库,在首层分别设置了一个单车道的入口和一个单车道的出口,是否满足两个汽车疏散出口的要求?

永锅 | 2023-06-29 12:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2023-06-29 13:30 00 [回复]举报

数量满足不少于2个的要求,单车道的型式规范认可,只要宽度满足要求不小于3米的话,满足汽车疏散出口的要求。


汽车库、修车库、停车场设计防火规范 GB50067-2014

6.0.9 除本规范另有规定外,汽车库、修车库的汽车疏散出口总数不应少于2个,且应分散布置。

6.0.13 汽车疏散坡道的净宽度,单车道不应小于3.0m,双车道不应小于5.5m。