地下商铺面积超过50平方需要设置几个安全出口

公共聚集场所,地下一层商铺,面积超过56平方需要设置两个疏散门吗?有没有规范指出,具体哪一条?

Courage_mTC5 | 2023-06-20 16:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2023-06-20 16:32 10 [回复]举报

那种“公众聚集场所”?非“歌舞娱乐放映游艺”的话,可以套用7.4.2.4或6的规定。


建筑防火通用规范 GB55037-2022

7.4.2 公共建筑内每个房间的疏散门不应少于2个。

儿童活动场所、老年人照料设施中的老年人活动场所、医疗建筑中的治疗室和病房、教学建筑中的教学用房,当位于走道尽端时,疏散门不应少于2个。

公共建筑内仅设置1个疏散门的房间应符合下列条件之一:    

1 对于儿童活动场所、老年人照料设施中的老年人活动场所,房间位于两个安全出口之间或袋形走道两侧且建筑面积不大于50㎡;    

2 对于医疗建筑中的治疗室和病房、教学建筑中的教学用房,房间位于两个安全出口之间或袋形走道两侧且建筑面积不大于75㎡;       

3 对于歌舞娱乐放映游艺场所,房间的建筑面积不大于50㎡且经常停留人数不大于15人;    

4 对于其他用途的场所,房间位于两个安全出口之间或袋形走道两侧且建筑面积不大于120㎡;    

5 对于其他用途的场所,房间位于走道尽端且建筑面积不大于50㎡;    

6 对于其他用途的场所,房间位于走道尽端且建筑面积不大于200㎡、房间内任一点至疏散门的直线距离不大于15m、疏散门的净宽度不小于1.40m。


“其他用途的场所”是指除儿童活动场所、老年人照料设施中的老年人活动场所、医疗建筑中的治疗室和病房、教学建筑中的教学用房和歌舞娱乐放映游艺场外的场所。