消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

四层以上歌舞娱乐场所是否每个房间都必须设置排烟

建筑防烟排烟系统技术标准 GB51251-2017 内4.4.12中规定 3 对于需要设置机械排烟系统的房间,当其建筑面积小于50㎡时,可通过走道排烟,排烟口可设置在疏散走道;排烟量应按本标准第4.6.3条第3款计算。

依上条,四层以上歌舞娱乐场所是否小于50平方米的房间内都不必须设置排烟。

如果是,走道房间排烟量应分别计算吗,

四层以上歌舞娱乐场机械排烟还应注意什么?

消防网友78337 | 2020-12-08 08:48
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

PQ 2020-12-08 11:43 10 [回复]举报

1、按烟规可以;

2、烟规4.2.1条文说明:采用隔墙等形成了独立的分隔空间,实际就是一个防烟分区和储烟仓,该空间应作为一个防烟分区设置排烟口,不能与其他相邻区域或房间叠加面积作为防烟分区的设计值。

可以只考虑走道排烟按4.6.3-3条执行。

3、烟规目前争议很大,各地地标有规定的可以参照,比如浙江对于上述情况要求走道排烟量不小于20000m³/H。

潘天坤 2024-06-18 16:59 00 [回复]举报

如果是一层至三层,可以按照楼主所说的按照烟规执行

按照建规和建筑防火通用规范要求:地上第四层及以上楼层的歌舞娱乐放映游艺场所应设置排烟设施

所以所有房间都应该设置排烟设施

走道和房间的排烟量应该分别考虑,并且要保证房间满足排烟要求

关闭

关闭

手机APP下载