消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

食堂防火门

开向建筑内食堂的防火门应为甲级还是乙级

消防网友5679 | 2023-04-12 12:40
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

张牙舞爪的张 2023-04-12 13:50 00 [回复]举报

正常建筑乙级,超高层建筑甲级。

消防老胡 2023-04-12 17:13 00 [回复]举报

使用明火加热方式的要设置乙级防火门,确有困难,可以使用防火卷帘。对于采用电加热的无明火的敞开式、明档类厨房可以不受此限制。注意:还需要设置防火挑檐(具体参看规范条文)

《建筑设计防火规范》(GB50016-2014,2018年)6.2.3 建筑内的下列部位应采用耐火极限不低于2.00h的防火隔墙与其他部位分隔,墙上的门、窗应采用乙级防火门、窗,确有困难时,可采用防火卷帘,但应符合本规范第6.5.3条的规定:…… 4 民用建筑内的附属库房,剧场后台的辅助用房;5 除居住建筑中套内的厨房外,宿舍、公寓建筑中的公共厨房和其他建筑内的厨房”和《饮食建筑设计标准 》(JGJ64-2017)4.3.10 厨房有明火的加工区应采用耐火极限不低于2.00h的防火隔墙与其他部位分隔,隔墙上的门、窗应采用乙级防火门、窗。 4.3.11 厨房有明火的加工区(间)上层有餐厅或其他用房时,其外墙开口上方应设置宽度不小于1.0m、长度不小于开口宽度的防火挑檐;或在建筑外墙上下层开口之间设置高度不小于1.2m的实体墙。

关闭

关闭

手机APP下载