消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教各位大神,下面地下车库排烟设计合理吗?一台风机保护两个防火单元且排烟与通风共用管道。

胡胡203 | 2023-02-15 11:29
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0

回答 | 4

王涛 2023-02-15 15:11 00 [回复]举报

一台风机能保护几个单元,要计算排烟量,能满足要求就行,排烟和通风是能共用管道的,平时用作通风,紧急情况要能自动切换为排烟状态。

消防黄河 2023-02-18 08:38 00 [回复]举报

理论是可以的。具体依据烟规设计。

胡胡203 2023-05-13 17:45 00 [回复]举报

如果恰巧在两防火单元中间位置起火,两边探测器均报火警,那么依照此设计理念,两侧的电动防火阀均被关闭,无法排烟。(火灾时联动关闭非起火单元的电动防火阀)

潘天坤 2024-08-06 09:11 00 [回复]举报

目前挺多地方认可电动汽车分散充电设施同一个防火分区的相邻防火单元可以共用排烟和补风系统,不过一般不能与其他非电动汽车分散充电设施共用系统,至于和平时通风合用只要措施设置到位应该是允许的,建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准
上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

关闭

关闭

手机APP下载