消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

外开式防火门能代替泄压口吗

外开式防火门能代替泄压口吗

风中沙 | 2022-09-26 16:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

永锅 2022-09-26 16:44 10 [回复]举报

 不同的气体灭火系统对泄压口的设置高度不一样,例如七氟丙烷灭火系统的泄压口应位于防护区净高的2/3以上;防火门的设置高度不满足要求;

防火门在喷放灭火剂前,应能自行关闭。

对不同类型的火灾,气体灭火系统对灭火浸渍时间都有一定的时间要求;防火门代替泄压口灭火剂流失量过大,起不到浸渍灭火的作用。

姜子牙疼 2022-10-11 16:06 00 [回复]举报

泄压口哪能用到门那么大的洞

关闭

关闭

手机APP下载