楼梯间开设疏散门

高层建筑的防烟楼梯间被隔壁的宾馆开设疏散门,作为宾馆的安全出口,是否许可?如果不许可的话依据的是规范的哪一条?

青皮果 | 2022-08-30 11:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

一成道人 2022-08-31 21:55 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版)

6.4.2.2 除楼梯间的出入口和外窗外,楼梯间的墙上不应开设其他门、窗、洞口。


周家斌 2022-08-31 22:15 00 [回复]举报

1、破坏了防烟楼梯间的防烟性能,正压送风考虑开门的数量,此处宾馆的门未设置前室。

2、复核楼梯间的疏散能力(宽度)

3、使用了非防火门,楼梯间墙体耐火极限被破坏了。