消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

单多层公共建筑首层疏散外门宽度?

《建规》5.5.30明确规定了住宅建筑首层疏散外门的净宽度,但5.5.18仅对高层公共建筑首层疏散外门做了规定,请问单多层公共建筑首层疏散外门净宽度应为多少?

消防网友37290 | 2021-07-21 10:26
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 8

天南地北 2021-07-22 09:02 00 [回复]举报

人密场所1.4米,一般场所1.1米

电梯   回复: 天南地北2021-07-22 18:56

首层疏散外门净宽度计算:人数 × 百人宽度 ÷ 100,然后与最小净宽度比较再取值。


这个1.4m特指“人员密集场所”的“人员密集的”,我理解为人员密集场所的人员密集的地方。见下面条文解释


5.5.19 观众厅等人员比较集中且数量多的场所,疏散时在门口附近往往会发生拥堵现象,如果设计采用带门槛的疏散门等,紧急情况下人流往外拥挤时很容易被绊倒,影响人员安全疏散,甚至造成伤亡。本条中“人员密集的公共场所”主要指营业厅、观众厅,礼堂、电影院、剧院和体育场馆的观众厅,公共娱乐场所中出入大厅、舞厅,候机(车、船)厅及医院的门诊大厅等面积较大、同一时间聚集人数较多的场所。本条规定的疏散门为进出上述这些场所的门,包括直接对外的安全出口或通向楼梯间的门。
本条规定的紧靠门口内外各 1.40m 范围内不应设置踏步,主要指正对门的内外 1.40m 范围,门两侧 1.40m 范围内尽量不要设置台阶,对于剧场、电影院等的观众厅,尽量采用坡道。


人员密集场所和人员密集的场所是两个不同的概念,详见下文。

https://b.1190119.com/article-1402.htm

0    0 [回复]举报

消防网友37290   回复: 电梯2021-08-02 16:00

请问这个单多层公共建筑首层疏散外门的最小净宽度规范中是否有明确规定?

0    0 [回复]举报

何青韦 2021-07-31 01:18 20 [回复]举报

题主明确说了是首层外门,规范规定了其他高层公共建筑的首层外门最小净宽1.2米,住宅建筑不小于1.1米。单多层公共建筑按危险性和疏散需求应是1.1之间。上面说的人员密集场所1.4米,不是首层外门,应该是指通向楼梯的安全出口的门。


何青韦 2021-07-31 14:01 00 [回复]举报

在根据疏散楼梯的净宽度要求,高层医疗建筑不小于1.3米,其他高层公共建筑不小于1.2米,住宅建筑不小于1.1米,一般公共建筑不小于1.1米。同上,单多层公共建筑的首层外门应不小于1.1米。

消防网友37290   回复: 何青韦2021-08-02 15:57

请问这个1.1m规范中是否有明确规定?

0    0 [回复]举报

乌伤浪人 2022-04-18 00:04 00 [回复]举报

这里规定的首层疏散外门是最低标准。疏散宽度还应按疏散人数、百人疏散宽度、楼层指标经过计算确定首层疏散外门的宽度。

消防黄河 2022-06-30 14:54 10 [回复]举报

不小于经计算的人员疏散宽度,且不小于0.9米。(若此门同时是人员密集的公共场所、观众厅的门时,且不小于1.4米。)

关闭

关闭

手机APP下载