消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

稳压泵与泵房的压差怎么处理

楼顶实验消火栓压力小 不符合规范,泵房管道压力达到了0.8.稳压系统还能否启动打压?请赐教   谢谢

消防网友3205 | 2021-07-10 11:17
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0

回答 | 4

林继青 2021-07-12 08:22 00 [回复]举报

稳压系统存在的理由就是为了保证最不利点灭火设施的压力要求,如果加压后压力超过了1.0,考虑分区

奖学金 2021-07-14 16:23 00 [回复]举报

      设置了稳压系统,按照规范要求,消防水系统最不利点静水压力就应该达到0.15MPa以上。

      如果你泵房使用的主管的镀锌钢管,耐压能力应该能达到1.6MPa以上。

      按照合法合规的要求,自然是要起泵运行。

      但在实际使用中,你首先应该考量整个水系统过去运行的状况,以前有没有承受过这么大压力?稳压泵起泵后,系统是否能保压,起泵间隔是多少?虽然规范起泵间隔是每小时15次,但是如果管道整体密封性能好,起泵间隔应该至少在几小时或者十几小时甚至几天以上。但是实际如果管道有渗漏,很容易保不住压,频繁起泵。

      必须修好整体管道,才能谈稳压泵启泵、打自动的事。

雨田 2021-08-01 15:06 00 [回复]举报

主干管上设置减压阀就行了

阳明心   回复: 雨田2023-04-10 15:39

主干管设减压阀的依据在哪里?可能不行的吧,会不会影响流量。

0    0 [回复]举报

关闭

关闭

手机APP下载