消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

报警阀组与正面墙的距离最小是多少?规范是不小于1.2米

报警阀组与正面墙的距离最小是多少?规范是不小于1.2米

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

EHS专家-DL 2025-05-13 08:33 20 [回复]举报

《自动喷水灭火系统设计规范》(GB50084)、《自动喷水灭火系统施工及验收规范》(GB50261)都有明确报警阀组正面与墙的距离不应小于1.2m。一般实际安装时建议预留15%的余量(即1.38m),以抵消施工误差和后期维护需求。

好记性不如烂笔头   回复: EHS专家-DL2025-05-14 22:04

正面距离墙这么远吗,我见好多正面距离墙不到1米

0    0 [回复]举报

EHS专家-DL   回复: 好记性不如烂笔头2025-05-15 12:11

那就是好多不规范

0    0 [回复]举报

陈泽平 2025-05-13 08:43 20 [回复]举报

5.3.1 报警阀组安装的位置应符合设计要求;当设计无要求时,报警阀组应安装在便于操作的明显位置,距室内地面高度宜为1.2m;两侧与墙的距离不应小于0.5m;正面与墙的距离不应小于1.2m;报警阀组凸出部位之间的距离不应小于0.5m。安装报警阀组的室内地面应有排水设施,排水能力应满足报警阀调试、验收和利用试水阀门泄空系统管道的要求。
      检查数量:全数检查。
      检查方法:检查系统试压、冲洗记录表,观察检查和尺量检查。

好记性不如烂笔头   回复: 陈泽平2025-05-15 00:24

湿式报警阀北面与墙面距离多少

0    0 [回复]举报

EHS专家-DL   回复: 好记性不如烂笔头2025-05-15 12:11

背面一般是紧贴墙面啊。

0    0 [回复]举报

大悟无言 2025-05-15 15:23 00 [回复]举报

如果是施工,则按GB50084GB50261要求来。如果是设计没有产品具体尺寸,可参考图集19S910-60所示来画图。

关闭

关闭

手机APP下载