丙类液体仓库与架空高压线的间距?有没有具体条文

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

wetom 2025-03-26 09:45 00 [回复]举报

规范确实没有明确提到丙类液体仓库与架空高压线的间距,根据建规及通规的条文解释理解,应按甲乙类仓库1.5倍电杆或电塔高度确定。

EHS专家-DL 2025-03-26 09:56 00 [回复]举报

丙类液体仓库与架空高压线的间距要求需结合电力安全和防火规范综合确定,具体如下:

  1. 水平安全距离要求
    丙类液体储罐与架空电力线路的最近水平距离不应小于电杆(塔)高度的‌1.2倍‌‌。此要求主要基于防止倒杆或线路断落引发事故的风险。

  2. 电压等级对应的最小间距
    根据电力行业通用标准,不同电压等级的高压线与建筑物之间应满足以下最小净空距离‌:

    • 10kV及以下‌:0.7米
    • 35kV‌:1.0米
    • 110kV‌:1.5米
    • 220kV‌:3.0米
    • 500kV‌:5.0米
  3. 规范条文依据

    • 《电气防火间距》中明确:丙类液体储罐与架空电力线路的间距需满足1.2倍杆高要求,且35kV以上线路与大型储罐间距需额外考虑(如超过40米)‌。
    • 电力设施保护相关规范规定了不同电压等级的最小净空距离,实际应用中需以电压等级对应的数值与1.2倍杆高中的较大值为准‌