消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

4平方米卫生间是否需要喷淋?

高规废除后,小于5平方米的卫生间是否都要装喷淋了?

| 2025-02-27 21:24
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消不动 2025-02-28 08:42 00 [回复]举报

没有强制性规定卫生间需要安装喷淋

潘天坤 2025-02-28 08:43 00 [回复]举报

建议按图施工,有设计即安装


如果属于需要设置自动灭火系统的场所,那么可以讨论下卫生间是否属于需要同时设置自动灭火系统的场所。有些人认为普通卫生间可燃物很少,属于火灾危险低的场所(建筑防火通用规范GB55037的条文说明及配套实施指南有提到可燃物很少的部位可以不设置),所以可以不设置自动喷水灭火系统,当然如果卫生间内存在比较多可燃物的情况还是要综合考虑自动灭火系统的


如果属于不需要设置自动灭火系统的场所,那么卫生间就不需要自动灭火系统啦,如果可燃物较多就考虑存放一些灭火器设施


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准





大恒 2025-02-28 15:44 00 [回复]举报

卫生间纸篓丢烟头着过火

小唐12321   回复: 大恒2025-02-28 15:55

这些都是小火,在火灾中,卫生间几乎没有

0    0 [回复]举报

关闭

关闭

手机APP下载