消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

气体灭火的事故后排风机控制箱设置在防护区内,是否需要在防护区外设置事故后排风机的手动控制装置,如果需要,可以套哪条规范条文呢?

事故后排风是否属于事故通风

吴浩 | 2025-02-26 11:51
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

潘天坤 2025-02-26 12:41 00 [回复]举报

气体灭火后的机械排风设施与事故通风设施是类似的,需要在室内和室外设置操作装置

可以根据所在场所性质选择对应规范,例如民用建筑选择《民用建筑供暖通风与空气调节设计规范》(GB50736-2012)第6.3.9条,工业建筑可以选择《工业建筑供暖通风与空气调节设计规范》(GB50019-2015)第6.4.7条

当然设置气体灭火的场所还可以选择《气体灭火系统设计规范》(GB50370-2005)第5.0.4条及第5.0.5条


吴浩   回复: 潘天坤2025-02-26 15:35

好的,受教了

0    0 [回复]举报

陈泽平 2025-02-26 15:32 00 [回复]举报

关闭

关闭

手机APP下载